I am looking at a control wire on an airfield. The wires are #14 and go between two vaults that are approximately 2 miles apart. They carry a 120V signal to a relay that turns a set of lights on and off.
Although it sounds like a small wire for that distance, the system worked for many years. There was an ice-cube relay at the end of the run and the current draw was low enough for it to consistently switch. However, the equipment was upgraded and a lighting relay put in place that will not latch.
I am certain that the problem is too high of an amperage requirement for the new relay, but there is an open issue that I need to understand.
During the testing, megger readings were taken of the wires. Both wires test properly to ground, but when they are meggered to eachother, a reading of around 55 k-Ohms is seen. Our initial thought was that there is weak insulation between the two wires at some point along the way, but the wires have been thoroughly tested again and we're not seeing a problem.
What I'm wondering is if the two wires running parallel for such a long distance could be causing the low megger readings. I can't put my finger on what the exact cause would be but my gut says that there could be something there.
Does anyone have any insight they can shed?
Although it sounds like a small wire for that distance, the system worked for many years. There was an ice-cube relay at the end of the run and the current draw was low enough for it to consistently switch. However, the equipment was upgraded and a lighting relay put in place that will not latch.
I am certain that the problem is too high of an amperage requirement for the new relay, but there is an open issue that I need to understand.
During the testing, megger readings were taken of the wires. Both wires test properly to ground, but when they are meggered to eachother, a reading of around 55 k-Ohms is seen. Our initial thought was that there is weak insulation between the two wires at some point along the way, but the wires have been thoroughly tested again and we're not seeing a problem.
What I'm wondering is if the two wires running parallel for such a long distance could be causing the low megger readings. I can't put my finger on what the exact cause would be but my gut says that there could be something there.
Does anyone have any insight they can shed?