Was out trouble shooting a motor that tripped on a startup today. Meggered the wires with the motor disconnected and disconnected at the starter. This is a 3-phase feeder in a underground PVC conduit.
The results are as follows:
1000V 60 seconds
A-B: 1.4 Gig ohms
B-C: 1.61 Gig ohms
A-C: 1.62 Gig ohms
A-G: 631 Meg ohms
B-G: 623 Meg ohms
C-G: 1.6 Gig ohms
The A-G and B-G does not seem right to me, but NETA states the minimum requirement is 100 Meg ohms. Does any one have any insights to these readings?
Thanks