bonding jumper

Senior Member
Is there a megger test standard? If somone wants to call for an electrician to test wires insulation where they may or may not have been exposed to damage, is there a testing standard that the electrician should go by?
"Electrician shall test wiring as per IEEE ???" or somthing along those lines.
Thanks very much.
 

ron

Senior Member
Re: Megger Test Standard

Electrician shall employ the services of testing agency that is a Full member of The InterNational Electrical Testing Association (NETA) to perform an insulation-resistance test utilizing a megohmmeter. Testing shall conform to the lastest version of the NETA Maintenance Testing Specifications.
 

earlydean

Senior Member
Re: Megger Test Standard

How about this?
IEEE Recommended Practice for Testing Insulation Resistance of Rotating
Machinery, IEEE Std 43-2000.

Also for field testing of medium voltage cables:IEEE 400 standard

And: IEEE P82, the Draft Test Procedure for Impulse Voltage Tests on Insulated Conductors.

all from the NETA web-site

Earl
 