What is the general rule of thumb minimum reading for feeder insulation testing?
I always forget
I always forget

I would not pass anything with those values. How old is that and what was it on?
That obsolete nameplate is posted here in the spirit of Internet Opinion (IO), under the Authority of Social Media & Angry Tolls (ASMAT).I would not pass anything with those values. How old is that and what was it on?
If no progress has been made on insulation materials over decades, sure, why not use these?
0.2A leakage on 1000Amp services appears to fail 30mA requirements of GFPE, but 20A/1M = 0.2mA appears to hold for 6mA Class-2 GFCI requirements.Lets see. . .800A/5K is 0.2 and 50A/250k is 2E-4. Maybe the ratios still hold.
That rule of thumb must originate from a more sophisticated engineering standard, not NFPA-70 or the NEC.Insulation resistance should be approximately one megohm for each 1,000 volts of operating voltage, with a minimum value of one megohm. For example, a motor rated at 2,400 volts should have a minimum insulation resistance of 2.4 megohms
I think it was IEC.That rule of thumb must originate from a more sophisticated engineering standard, not NFPA-70 or the NEC.
It was www.transcat.com not IEC..That rule of thumb must originate from a more sophisticated engineering standard, not NFPA-70 or the NEC.
Can't find it. Is there a direct link?It was www.transcat.com not IEC..
Can't find it. Is there a direct link?