Megger time!!!

Status
Not open for further replies.

Charlie Bob

Senior Member
Location
West Tennessee
I'm gonna start trying out my fluke 1587.
So, I'm gonna megger my new service job first then my branch circuits.
1- Feeders meggering.
- disconnect load side (2 hots , 1 neutral and EGC) from main 200 amp disconnect outside.
- No need to disconnect line in 200 amp panel box inside.
-Then megger L to L, L to N, L to G, N to G.

2- Branch circuits.
-Unscrew light bulbs from temporary pig tails.
-In Panel Box , disconnect hot to breaker from circuit to be tested, disconnect neutral from bar, and disconnect ground as well.
- Now test H to G, H to N, N to G.

A - Does this sound ok to you all?
B - Could i have left the ground hooked to ground bar and test that way?
C - If i leave the ground hooked then wouldn't the main grounding jumper at main disc. mess my readings?
D - Anything else i missed?

Thank you all.
 