Meggering Existing Wiring

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hey Guys,
When Meggering the existing wiring low voltage wiring, are you looking to be read above a specific ohmic value to conclude that the insulation is OK? Can a megger test further compromise the existing wiring?
Thanks,
EE
 
By low voltage do you mean conductors with 600 v insulation?
HVAC techs that work on 24v consider 120 to be high voltage….
 
Last edited:
One testing manual has the following voltage recommendations for insulation testing.
Normal circuit voltageTest voltageMinimum resistance
Between 0 V to 50 V AC250 V DC0.5 MΩ
Between 50 V to 500 V AC500 V DC1 MΩ
Between 500 V to 1000 V AC1000 V DC1 MΩ
 
Once you have isolated the wiring from all equipment, the greatest risk I see of increasing existing damage to wiring would be if the damage is already severe enough to fail the megger test and required replacement.
 