Meggering question

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
If you have a 240V circuit underground in PVC and every time it rains you are having a issue with the breaker tripping, should I megger the wires when it is not raining, or when it is raining? Can a megger detect damage on the insulation of a single wire, even if it is dry and not leaking any current? Don't have much experience using them. Thank you for your help.
 

brian john

Senior Member
Location
Leesburg, VA
A conductor with damage insulation in PVC can be the one tough item to catch with a megger. I would shoot for when it trips and in your case that is when it rains.

Though unless the conduit is arranged to drain (damaged) it seems the water should be present most of the time.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
If you know the problem is in a wet conduit, replace the wires. A megger is only going to confirm it, and the wires will still need to be replaced.

On long buried runs we can usually find the problem with a fault finder. The pvc is generally cracked in the immediat area of the fault.
 