Megging conductors in cable tray/cable bus

Status
Not open for further replies.

joshuablake48

Member
Location
All across the country
Occupation
Journeyman Electrician
I believe my entire company has been using a megger incorrectly and I would like an answer on whether or not I am correct or not.
We are running superior cable bus with 30 RHW conductors and the tray has a 600kcmil bare aluminum clamped to it so the bus is the EGC.
We are required to Meg all conductors before terminating using fluke megger at 1000v for 1 minute on each conductor. I was told to use another conductor as a common - black lead, the of course red lead on the conductor im megging. I only get a reading that says OL- open line.
My understanding after researching is the black lead would need to be attached to the cable bus in order to read the leaking voltage in the case of damaged insulation. But the cable bus outside does not have the covers on yet so if there is any damaged insulation not right up against the bus the megger will just read open line- so my question is, will a megger properly work if the wire is not in a completely enclosed mettalic Raceway? Shouldn't I be getting an actual number instead of the megger just going to infinity and saying OL? What would the proper way to Meg these conductors if I am doing it incorrectly? Thank you for any assistance.
 
Depends.

Checking for faults between specific cables, you would use the cables. Cable to tray, cable to tray.

You can have a bare spot on any conductor and it will still test good at that moment, if it is not touching something and it is dry. Cable to cable or tray.
 
Depends.

Checking for faults between specific cables, you would use the cables. Cable to tray, cable to tray.

can have a bare spot on any conductor and it will still test good at that moment, if it is not touching something and it is dry. Cable to cable or tray.
That's what I'm trying to tell my superiors. This cable bus has cleats that separate all the conductors by about an inch, so it would make it impossible for the wire to touch another conductor or the bus. I'm thinking it's a giant waste of time as we have 2400 wires total. I think if I just terminate everything and then ohm out phase to ground just to make sure there is not a bought for the installation is jammed into a corner of the tray that would suffice. But specs are specs and I will probably have to do it anyway
 