ptonsparky
Tom
- Occupation
- EC - retired
Fire Job.
I have talked about a Forensics Engineer taking samples of smoke deposits on/in a transformer. While he was there we megged the 208 3ph panels with all the breakers off. He was gone getting some supplies for his test so for the hell of it I put the megger leads on the insulation of a larger set of wires leaving this enclosure then repeated this "test" on his return. Clamped to the insulation about 8" apart. While the readings are still high, it is pretty obvious they don't match up to a similar length of new that we compared it with.
Have any of you tried this on older installations that just had an accumulation of dust? Do you remember what you had? I know this is comparing apples to oranges.
A set of paralled feeders that also "failed" totals about 2000' of 300MCM CU.
Any way to clean the carbon from them that would make you feel good about hooking them back up?
I have talked about a Forensics Engineer taking samples of smoke deposits on/in a transformer. While he was there we megged the 208 3ph panels with all the breakers off. He was gone getting some supplies for his test so for the hell of it I put the megger leads on the insulation of a larger set of wires leaving this enclosure then repeated this "test" on his return. Clamped to the insulation about 8" apart. While the readings are still high, it is pretty obvious they don't match up to a similar length of new that we compared it with.
Have any of you tried this on older installations that just had an accumulation of dust? Do you remember what you had? I know this is comparing apples to oranges.
A set of paralled feeders that also "failed" totals about 2000' of 300MCM CU.
Any way to clean the carbon from them that would make you feel good about hooking them back up?