Bassclefjef
Member
- Location
- Woodlands,Texas
I have a 1200 amp GFP breaker feeding two chillers. Having a nuisance problems with high current shut down after a tree fell on a power distribution lines. I hired an electrical contractor to meg parallel underground feeders. They said A phase and B phase meg together and to ground. The 1200 GFP breaker never trips. The company did not disconnect load side feeders from 1200amp GFP breaker when tested. My question is, "Wouldn't it be necessary to disconnect the conductors from the load side of breaker due to the GFP sensors giving a false reading not to mention possible damage to the GFP sensors?" Voltage is steady on all 3phase when chiller is running. Amperage just starts climbing until chiller shuts itself down after about 15 min of runtime.