megging pump/motor- Bad call for repair?

Status
Not open for further replies.

jimbo123

Senior Member
We removed a sump pump motor from a pit to check because of tripping the cb Motor has been in service for about a year now, cycles every 20 minutes or so , 5 days a week , 8 hrs a day.
We checked the motor and found the cable attached to the control box to the motor was damaged . It appeared cable were nicked near the pump inside the pit.
We removed all but 4' of cable to test motor winding before sending it out for repair.
We used a fluke 1587 to test motor. We megged motor and got a reading of .4 megs . Also found continuity from winding leads to egc and case of motor .
Outside shop reported empeller was eaten away but windings were ok. We also compaired our reading to the alternate pump in same pit . Motor had a reading of over 1 gig. Both are 7.5 hp 480v. Where did we go wrong with our call ?
 

brian john

Senior Member
Location
Leesburg, VA
Could have been the cable into the housing, it depends on how they tested the motor.

You meggered conductor to conductor
phase to phase-should be dead short
phase to ground
Correct?
And you meter is calibrated?
 

jimbo123

Senior Member
No i meg each of the 3 conductors to ground.
And continuity test from conductor to ground and then winding to winding.

Thanks for the help.
 