Have the wires capped off on one end, meg wire to wire, meg ground to wire. It does the same thing every time it fluctuates constantly.
I believe the motor has been disconnected, but yes, I've had fan motors turning in the wind do that.Is the motor turning? It can easily happen if it is a fan resulting in a fluctuating reading. Another thing to watch out for is polarity in case there are damp, exposed conductors. Galvanic action can cause a DC voltage between the conductors and ground. One polarity can give a higher reading than the other. When in doubt, test with positive and then with negative to ground.
Let's look at this again. First, you only need 2 megs to pass on 600vac wire. So this is not a show stopper. Second, gotta wonder if it is a instrumentation problem. Got fresh batteries in the megger? Got another megger you can verify with. Third, what else could be going on? Are the ends of the conductors nice and clean? (damhik...). Could the conduit be part of a ground loop, causing a voltage to be induced in the conductors? Is there nearby equipment that could be turned off to see if there is interference? Are there other conductors in the conduit? Is the ground conductor disconnected? (Sorry, had to ask.) Lastly, might be one of those eternal mysteries.What does this mean? Thank you for your help. BTW, I separated the wires from the VFD, separated the wires from the motor. Have the wires capped off on one end, meg wire to wire, meg ground to wire. It does the same thing every time it fluctuates constantly.