Megohmeter measurements ?
Danny89
Indian Land
What is a good guideline basis with using a megohmeter.
Example...
Above this # your good...
Below this # your insulation is compromise d.
Thanks in advance,
Danny
Sent from my Moto Z (2) using Tapatalk
I don’t work to the NEC, BS7671 cites 1MΩ as minimum which I don’t agree with.
I worked to M&Q (Mines and Quarries) regulations where they give “the maximum leakage current is not to exceed 1/10,000th of the circuit FLC”. With older high current circuits you know the acceptable limits.
Example...
Thanks in advance,
Danny
All depends on what you are testing, there have been several good threads about this topic here if you use the search function.
Per the others, we follow the procedure for the type of wire being tested. Spec. was spelled out.
Once again it depends, a new circuit with just 1MΩ to earth/ground there is something wrong, an old circuit it may be acceptable.
A point many people get wrong is not allowing enough time for a circuit to charge, at first glance it reads low, wait a while the reading rises.
Yes. "Circumstances alter cases" as Just William said.
I was at a paper mill where the field on one of the DC motors was under 100 kohm. Not acceptable I thought. The mill engineer said it was OK and would come up once the field had been energised for a while. He was right. It did. Paper mills are very wet places.
Example...
Thanks in advance,
Danny
Contact the manufacturer of the wire or cable. They (we) always have specific recommendations and guidelines that can be provided for the customer. Always remember that in MEG testing, if everything is insulated and the raceways are nonmetallic (same for sheathing) then the chances of getting reliable readings are slim. Unless of course there is damage at mutual locations in the raceway or cable assembly. Good Luck.