I have (2) 4350 KVA 575 volt transformers feeding an electric melt furnace. (8000 amp)
Anyone here had experience with such that is willing to accept a few I.M.s ?
 
power guy

power guy

I'm a power system fault, coordination and arc flash guy Augie. Melt furnaces are controlled arc flash sources.
I know they're low power factor loads, and need a stiff Utility power source, or they'll reak havoc on Utility distribution systems.
I'm on the road all day tomorrow, but would be happy to provide an assist Thursday, if it's up my alley.
IM/PM me.
John M
 
I have (2) 4350 KVA 575 volt transformers feeding an electric melt furnace. (8000 amp)
Anyone here had experience with such that is willing to accept a few I.M.s ?
I've had some dealings with arc furnace controls.
But quite a long time ago - the steel industry in UK has all but vanished.
 
Is it an arc or induction furnace?

No even sure about that, From conversations, I assume ARC, Right now its a hole in the ground amd some 161k towers going up.
The preliminary print shows an AIC SCR furnace controller.
The drawings show some unusual grounding about which I have questions,
 
No even sure about that, From conversations, I assume ARC, Right now its a hole in the ground amd some 161k towers going up.
The preliminary print shows an AIC SCR furnace controller.
The drawings show some unusual grounding about which I have questions,
At 4,350 kVA it seems a bit small for an arc furnace.
The ones I dealt with were in the tens of MW. The last was a 114MW.
They had a dedicated 132kV supply, separate from the rest of the steel mill.

On another tack, 4350 kVA isn't 8kA (assuming the supply is 575V 3ph).
 
Most of the controversy revolves around bonding.
The (2) 575 v transformers are customer owned and supplied by customer owned 12kv so we are dealing with an SDS.
The furnace folks are adamant about the grounding means so as to "prevent ground loops".
They want no grounding, grounded, bonding conductors routed thru the conduits or the cable tray.
All grounding is accomplished by an extensive grounding grid with singular runs to each piece of equipment to a common ground buss.
 