An interesting problem. On a residential hot water heater the lower element has burned out every four months for the last two years. The owner saved the elements and showed them to me. The outside jacket had melted away, leaving a drip of copper on the end of the burn.
Obviously when the element shuts off water gets into the center of the element and the when it starts again this water boils and blows large tares in the length of the element.
I have seen them blow apart before but never melted. Water should suck the heat away two fast to allow it to melt, let along drip copper.
Specifics:
Water Heater
60 gallon
(2) 4500 watt elements
(2) thermostats (one for each element)
240 Volts
Supply Power:
Voltage: 246
Current: 24 Amps (when both elements are working)
Cold to Hot time: 1 hour 10 min.
Wire Size: #10 Copper
Breaker: 30 Amp
Other than the element size I find nothing to question.
My theory is that the element is getting hot enough to create a boiling water effect around it or part of it. This allows the element to over heat because it is like being in an air pocket.
What do you think?
Loren
Expert Electrical Services
Obviously when the element shuts off water gets into the center of the element and the when it starts again this water boils and blows large tares in the length of the element.
I have seen them blow apart before but never melted. Water should suck the heat away two fast to allow it to melt, let along drip copper.
Specifics:
Water Heater
60 gallon
(2) 4500 watt elements
(2) thermostats (one for each element)
240 Volts
Supply Power:
Voltage: 246
Current: 24 Amps (when both elements are working)
Cold to Hot time: 1 hour 10 min.
Wire Size: #10 Copper
Breaker: 30 Amp
Other than the element size I find nothing to question.
My theory is that the element is getting hot enough to create a boiling water effect around it or part of it. This allows the element to over heat because it is like being in an air pocket.
What do you think?
Loren
Expert Electrical Services