We are looking to use Meltric switch-rated connectors for some 3-phase motors on an industrial installation. don't think there are any issues with these since they're CSA-rated, etc. but what about free working space requirements? I don't think it's required since the connectors themselves are dead front so they really don't need to be treated any differently than a standard receptacle?

The reason I'm asking is these connectors would be mounted on the wall and you'd have to step over the motor to comfortably disconnect this connector.

Any concerns with LOTO?

Meltric DN & DNS connectors
Screenshot 2024-11-08 141048.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
They are great for lotto...the male end has a place to install a lock so it cannot be inserted into a receptacle.
As far as 110.26(A) workspace, there will be opinions on both sides and the only one that counts is the one your AHJ holds.
 