Working on a near total outage in one of our large plants in order to upgrade DCS. After upgrade in process of bringing plant back up, testing equipment, interlocks, etc. Walk into control room and ask if there is anything they need us to look at and the entire plant suddenly goes dark.
To make a long story short, "Breaker Closed" lightbulb on Cutler-Hammer 1200A 480V breaker was burned out and being replaced. Apparently the lamp is in parallel with the NO trip coil contacts and is a high impedance lamp. Replacement lamp was incorrect impedance and shunted trip contacts tripping the breaker which fed the lighting transformers for the plant. Good news is we found a UPS (dead battery holder) that was no good. Talk about exciting...
To make a long story short, "Breaker Closed" lightbulb on Cutler-Hammer 1200A 480V breaker was burned out and being replaced. Apparently the lamp is in parallel with the NO trip coil contacts and is a high impedance lamp. Replacement lamp was incorrect impedance and shunted trip contacts tripping the breaker which fed the lighting transformers for the plant. Good news is we found a UPS (dead battery holder) that was no good. Talk about exciting...