J jbolen Senior Member Jun 2, 2020 #1 Question: I have 4/0 box attached to a 3/4 rigid conduit that is supported 3 ft. from the box is more support required. This for a motion sensor
Question: I have 4/0 box attached to a 3/4 rigid conduit that is supported 3 ft. from the box is more support required. This for a motion sensor
S SSDriver Senior Member Location California Occupation Electrician Jun 2, 2020 #2 If I remember correctly I believe you need two conduits to support a Box
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 2, 2020 #4 The only time a raceway can support a box is when the box has threaded hubs. 4" box requires it's own support.
The only time a raceway can support a box is when the box has threaded hubs. 4" box requires it's own support.