what is the best way to actually connect the bond required at a metal framed building?
contractor is proposing to use an anchor bolt, (inset bond wire under it and tighten down)
what have you seen/done?
thanks!
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
(B) Methods Not Permitted. Connection devices or fittings that depend solely on solder shall not be used.
so would it qualify as described under #5?
thanks!
Yeah, I can just see someone bending a U in a 1-0 and hooking it under a washer and nut. :roll:I would be concerned with inserting a copper wire between the nut and washer and the base of a structural column. You might have a hard time getting a structural engineer to accept it.
Yeah, I can just see someone bending a U in a 1-0 and hooking it under a washer and nut. :roll:
No silly, you would use a #14 tap conductor!:grin::grin: