I don't think you'll find much that will tell you where you MUST use it. You will, however, find prohibited locations for type NM cable. MC is the first choice for locations where type NM cable is prohibited. You might want to read about NM prohibited locations, and that will give you a head's up on where to use MC.catskills said:....i can't find anything that spells out exactly where you need to use it.
Indeed. Article 334 is all about NM cable, and 334.12 covers the uses not permitted. If there is a location in 334.12 that is not permitted for NM cable and it's not listed in 330.12 (prohibited locations for type MC cable), MC cable would be a good first choice. You can always use a better method (EMT, IMC, RMC), but certain economic realities begin to prevail.catskills said:thanks Marc. do you know what section lists the prohibited use of nm?
catskills said:I'm just looking to find where it is required to be used as opposed to nm cable. I know of places of assembly, commercial locatiobs, buidlings over 3 stories, etc. i can't find anything that spells out exactly where you need to use it.
What year NEC is your area using? (You're in Catskills, NY?)catskills said:I'm just looking to find where it is required to be used as opposed to nm cable. I know of places of assembly, commercial locatiobs, buidlings over 3 stories, etc. i can't find anything that spells out exactly where you need to use it.
2005 NECH, commentary following 334.10A well-established means of codifying fire protection and fire safety requirements is to classify buildings by types of construction, based on materials used for the structural elements and the degree of fire resistance afforded by each element. The five fundamental construction types used by the model building codes are Type I (fire resistive), Type II (noncombustible), Type III (combination of combustible and noncombustible), Type IV (heavy timber), and Type V (wood frame). Types I and II basically require all structural elements to be noncombustible, whereas Types III, IV, and V allow some or all of the structural elements to be combustible (wood).
The selection of building construction types is regulated by the building code, based on the occupancy, height, and area of the building. The local code official or the architect for a building project can be consulted to determine the minimum allowable (permitted) construction type for the building under consideration. When a building of a selected height (in feet or stories above grade) and area is permitted to be built of combustible construction (i.e., Types III, IV, or V), the installation of nonmetallic sheathed cable is permitted. The common areas (corridors) and incidental and subordinate uses (laundry rooms, lounge rooms, etc.) that serve a multifamily dwelling occupancy are also considered part of the multifamily occupancy, thereby allowing the use of nonmetallic sheathed cable in those areas.
If a building is to be of noncombustible construction (i.e., Type I or II) by the owner's choice, even though the building code would permit combustible construction, the building is allowed to be wired with nonmetallic sheathed cable. In such an instance, nonmetallic sheathed cable may be installed in the noncombustible building because the Code would have permitted the building to be of combustible construction.
Annex E provides charts and other explanatory information to assist the user in understanding and categorizing the exact types of construction under consideration. A table to cross reference building types to the various building code types of construction is provided in Annex E also.
FPN No. 2:See Annex E for determination of building types [NFPA 220, Table 3-1].
Very true. There are locations where NM is also permitted, which would be cheaper. There are locations where MC would be permitted, where EMT is more traditionally installed. That one's a toss-up. Looks/tradition versus ease of install. Just because type MC cable is permitted in certain locations doesn't necessarily mean that it's a good idea.iwire said:There are very few places MC is not allowed.
That's the basis for us so often saying that we're allowed to do that which is not prohibited.wbalsam1 said:It's more like process of elimination than anything to solve for allowable wiring methods.![]()
LarryFine said:That's the basis for us so often saying that we're allowed to do that which is not prohibited.
tom baker said:For office buildings, I don't like MC as it leaves no future additions as EMT does.