The bus duct is often on the secondary side of a lager transformer and on the load side of the secondary OCPD. It takes a lot of secondary current to trip the transformer primary OCPD.
The plant I often work is working on the replacement of their outside bus duct runs with cable bus as a result of a couple of failures related to water ingress.
i've installed both, and it's pretty hard to beat a cable with a swaged lug on the end of it.
if all you are doing is moving a bucketload of power without needing to tap it along the way,
it's pretty unbeatable.
largest bus duct install i've worked on was hughes electro optical, in el segundo, calif.
a long while ago.... they had a large amount of problems with the system, i'd say
2/3 labor, but 1/3 was moisture.
stuff got wet. they tried a lot of solutions including putting 1,000 amps at 12 volts thru
a 3,000 amp bus duct to warm it up and dry it out. they tried blowers, heaters, etc.
so, moisture is the nemesis. i never did understand why on earth they didn't megger each
piece before putting it into the system, and megger the entire bus after each torquing.
must have had something to do with 400 electricians working with the tools, on 7-12's. :huh: