Metal Garage Bonding/grounding

Status
Not open for further replies.

WCoughlin

New User
Location
Canada Ontario
Occupation
Master Electrician
Good Morning Guys I'm currently working on a project where I'm running a 100amp branch cct from a 200 amp main panel inside the house to a panel located in the garage the frame is steel and is bolted to the concrete floor which was poured before I got the project. With that said Do I need to provide a ground rod to the structure with a loop? would I be ok with a ground rod and one point of connection or can I run a bond from the new 100 amp panel to the frame? Thanks for your time and help.
 

Eddy_Current

Member
Location
Canada
No you are not allowed to install another ground rod at the garage in Canada. You must run a bond from the main panel out to the new panel. You will also have to bond the steel to the new panel
 