Metal halide lamps

Status
Not open for further replies.

Sahib

Senior Member
Location
India
In an indoor auditorium wiring project, metal halide lamp fittings were used in ceiling as a cost cutting measure to reduce number of fittings with LED fittings fixed on side walls. During a power point presentation that was mentioned. I expressed my appehension that a metal halide lamp is laible for violent failure and should not be used in such applications. Your comments please.
 
I am surprised an auditorium went with a lamp type that is poor for dimming and has a restrike time.

As far as end of life failure I would not be concerned, MH lamps are used indoors often.
 
Last edited:
In an indoor auditorium wiring project, metal halide lamp fittings were used in ceiling as a cost cutting measure to reduce number of fittings with LED fittings fixed on side walls. During a power point presentation that was mentioned. I expressed my appehension that a metal halide lamp is laible for violent failure and should not be used in such applications. Your comments please.
NEC recognizes this as well. If the luminaire doesn't have an enclosed lamp then you must use a lamp designed for open luminaires. They are designed to not rupture as easily during such failures and are designated with "type O". 410.130(F)(5)
 