metal lite pole egc

Status
Not open for further replies.

stew

Senior Member
Does anyone know of any additional code requirements for light pole egc size beyond what is in 250 ? Are there any specific requirements that would require anything larger than #6?
 
Does anyone know of any additional code requirements for light pole egc size beyond what is in 250 ? Are there any specific requirements that would require anything larger than #6?

250.122(B) might require the EGC to be 6 or larger.

What size are the circuit conductors?

What size breaker?
 
30 amp breaker for one pole 20 amp for the other and 20 for the parking lot lite. current is 22.5/15/7.5. wire size is 6 for the 30 amp load due to length. and 8 for the 15 amp load due to length and 10 for the 7.5 amp load. using a 10 egc.
 
Status