Metal rigid as support

Masshearer

New User
Location
Tampa fl
Occupation
Electrician
I have used 2 metal rigid conduit post with strut between them as a support for bell box and separate conduit on rooftop receptacles in the past. I was questioned whether this would pass which it has but could not prove it was legal per nec. So now I’m asking the others to chime in.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If I picture it correctly it appears to comply with 314.23(F) if both conduits are threaded into the enclosure.
 
Top