NEC 250.104(a)(1) refers to Metal water piping, but it is not clear that this metal piping is a water pipe used for an electrode system. This section has you size it by an elcectrode system table 250-66.
I have an inspector saying that a plastic well to metal water pipe falls into this section.
I say that it falls under 250.104(b) which is other metal piping and an equipment ground. He says the word "Other" clearly means other than water pipe and I say "Other" means other than an electrode pipe. Has anyone run across this.
It just doesn't make sense to size an non-electrode pipe to a table for electrode pipes. This pipe is no different than any other pipe in the house which is sized by an equipment ground.
I have an inspector saying that a plastic well to metal water pipe falls into this section.
I say that it falls under 250.104(b) which is other metal piping and an equipment ground. He says the word "Other" clearly means other than water pipe and I say "Other" means other than an electrode pipe. Has anyone run across this.
It just doesn't make sense to size an non-electrode pipe to a table for electrode pipes. This pipe is no different than any other pipe in the house which is sized by an equipment ground.