Have a Non-Hazardous electrical room adjacent to Cl 1, Div 1, Gp D Classified Location. All Electrical distribution gear is installed in the non-hazardous location. Problem: All metal water pipe is located in the adjacent Classified location only and should be electrically bonded. How can this physically be done and still meet intent of NEC? If bonding jumper was routed through barrier wall it would require metallic conduit. Therefore it needs a seal-off @ the barrier wall. How can the bonding jumper be physically bonded to the conduit at both ends to satisfy 250.64. Another issue: what is done within the hazardous location for termination at the water pipe system? Is a standard pipe saddle-clamp used in the hazardous location? It wouldn't have a specific listing for the environment.