A metal frame of a building can be an electrode as described in 250-52(A)(2) but can a metal tray system that is labeled "UL approved for equipment grounding" also be an electrode when effectively grounded like the metal frame of a building?
392-7 tells me "Metallic cable trays...shall be grounded as required...in accordance with 250-96"
250-96(A) tells me "...cable trays...that are to serve as grounding conductors...shall be effectively bonded..."
Looks like an effectively bonded tray system IS the grounding conductor, or is it [can it be] the electrode like a building metal frame?
Can I terminate a properly sized GEC from a transformer to an effectively bonded tray system, and will this GEC be considered unbroken when doing so?