Metallic Conduit on Roof-Tops Will Require an EGC!

Status
Not open for further replies.

joe tedesco

Senior Member
250.118, Exception: Where metallic conduit is installed on rooftops, an equipment grounding conductor of the types specified in 250.118(1) shall be provided within the raceway and
sized per Section 250.122. [ROP 5?211]

250.118(1) A copper, aluminum, or copper-clad aluminum con-ductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.

Shouldn't this read "metal conduit or tubing"?

I have many images where EMT is pulled apart on rooftops! I have not seen any "threaded" connections pull apart!

Opinions?

[ July 29, 2003, 08:55 AM: Message edited by: joe tedesco ]
 

ron

Senior Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

Although the Code does not define the word conduit, I have always included EMT (tubing) under the umbrella definition of conduit. The Code does list EMT under the "conduit" index listing in the back of the book.
 

joe tedesco

Senior Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

Ron:

See Table 1 Percent of Cross Section of Conduit and Tubing for Conductors, Table 4 Dimensions and Percent Area of Conduit and Tubing (Areas of Conduit or Tubing for the Combinations of Wires Permitted in Table 1, Chapter 9) and Annex C and where the word "Tubing" is specific.

Also, the term "conduit or tubing" appears throughout the code, such as in the definition of "Conduit Body", 300.15(C), 402.7, 426,22(C), 527,4(G), 550.15(F), 551.47(B), and more can be found search for "conduit or tubing" in the NEC.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

With UL removing the raintight listing for EMT fittings this may be a moot point. :D

IMO EMT is never a good choice for roof top use as I have seen many installations where the EMT has rusted through entirely or as Joe said, been kicked apart at couplings or connectors.

But back to the question.

Even in the article 100 definition of a conduit body
Conduit Body. A separate portion of a conduit or tubing system that provides access.....
they feel the need to say conduit or tubing system.

So I would have to agree with Joe that for this article to have a useful effect it would have to say "metal conduit or tubing"
 

bennie

Esteemed Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

According to 358.12 EMT is not approved where it is subject to severe physical damage.

This is why there is no specific reference to EMT. It should not be installed on an accessable roof area.
 

ryan_618

Senior Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

Originally posted by bennie:
According to 358.12 EMT is not approved where it is subject to severe physical damage.

This is why there is no specific reference to EMT. It should not be installed on an accessable roof area.
Bennie: I've been wrong before, but I would view "severe physical damage" as a forklift hitting the EMT, not someone accidently tripping over it.
 

joe tedesco

Senior Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

5-211 Log #2293 NEC-P05
(250-118(14) Exception (New) )
Final Action: Accept in Principle

TCC Action:

See the Technical Correlating Committee Note on Proposal 5-1. The Technical Correlating Committee notes that the issue of
determining acceptability for the particular wiring method for grounding is the responsibility of the applicable Code-Making Panel.
For this proposal, Code-Making Panel 8 has the responsibility to determine if the wiring method is acceptable as proposed. The
Technical Correlating Committee refers this proposal to Code-Making Panel 8 for comment.
Submitter: Norman Smith, I.B.E.W. Local 291 / Rep. Labor
Recommendation:
Insert after Section 250.118(14).
Exception: Where metallic conduit is installed on roof tops, an equipment grounding conductor shall be provided within the raceway
and sized per Section 250.122.
Substantiation:
Metallic conduit on rooftops is exposed to extreme temperature changes and weather conditions and may lose electrical continuity at
connections and the capacity to conduct safely any fault current likely to be imposed on them.
Panel Meeting Action: Accept in Principle
Revise the text to add an exception to 250.118 located after 250.118(14) to read as follows:
Exception: Where metallic conduit is installed on rooftops, an equipment bonding conductor of the types specified in 250.118(1) shall
be provided within the raceway and sized per Section 250.122.
Panel Statement:
This issue has been raised with varying amounts of technical substantiation for several Code cycles. The problem being identified
really relates to an unsuitable use and installation of this wiring method leading to these conditions. The panel understands the safety
concerns raised by the submitter's substantiation. CMP 5 requests the Technical Correlating Committee to refer this proposal to CMP 8
for action.
Number Eligible to Vote: 16
Affirmative: 12 Negative: 4 Ballot Results:
Explanation of Negative:
BRETT: The submitter has not provided technical substantiation for this proposed change. His statement is true that weather conditions
exist on rooftops. However, the present language in the code already covers these installations. Proper installations in accordance with
present code language take all these conditions into consideration.
The panel actions taken have not been substantiated. All proposals over the past several code cycles have cited workmanship issues
relating to small sizes (1/2 and 3/4) of metallic and nonmetallic unthreaded raceways being improperly installed.
The code has always required raceways to be properly supported and secured. 300.7(B) states: "Raceways shall be provided with
expansion fittings where necessary to compensate for thermal expansion and contraction." All raceways are required to be listed. RMC,
IMC and EMT are listed galvanized steel raceways and provide corrosion protection. Physical protection is also adequately addressed in
each code article.
The change as accepted would require all metal raceways to have an equipment grounding conductor installed including threaded
raceways up to trade size 6. What substantiation has been provided to require threaded metal raceways to have a supplemental equipment
grounding conductor? These requirements would also apply regardless of the purpose i.e., Service, Feeder, Branch circuit, etc.
The change is overly restrictive and the responsibility should remain with the designer. Please reject this proposal.

DOBROWSKY: The submitter's substantiation indicates that the wiring method chosen for this specific installation was not suitable.
Even if an equipment bonding conductor was installed if the wiring method was damaged, the conductors would be exposed creating a
hazard. Many existing wiring methods have been safely used for many years without an additional equipment bonding conductor.

SKUGGEVIG: The same harsh conditions that jeopardize the electrical continuity of the metal raceway will also act to cause failure of
the equipment grounding conductor (wire) after the raceway has failed leaving sections of the wires exposed. A supplementary
equipment grounding conductor might be unable to sufficiently improve the overall reliability of the dual grounding path, and does not
address the problem of keeping all of the conductors fully protected inside of an intact raceway. The problem of dealing with a harsh
environment cannot be solved by simply adding another vulnerable and marginally protected component into the harsh environment.
The metal raceway must be made more resistant to failure in the harsh environment if it is to be used in this environment. If this is
accomplished, then there is nothing wrong with the metal raceway's ability to serve as the sole grounding path, without a supplementary
grounding conductor. In addition, see my Comment on Affirmative on Proposal 5-1 regarding changing the term "equipment grounding
conductor" to "equipment bonding conductor".
STEINMAN: There is no technical substantiation provided to make this change. The substantiation provided by the submitter is a
violation of 300.7(B), "raceways shall be provided with expansion fittings where necessary to compensate for thermal expansion and
contraction." Properly installed, metallic raceway systems are good equipment grounding paths.

Comment on Affirmative:

RAPPAPORT: The word "conduit" should be replaced with the generic term "raceway" in order to include electrical metallic tubing.

TOOMER: The panel recognized there is a problem, therefore since it has the authority, it should require an equipment bonding
conductor be installed for safety.
594
 

bennie

Esteemed Member
Re: Metallic Conduit on Roof-Tops Will Require an EGC!

The EMT pulling apart, from persons stepping on it, is proof enough that the wrong wiring method was used. By including EMT in the ground conductor issue, it would be taken as approval of the wiring method.
 