Metallic LB fitting

Merry Christmas

nizak

Senior Member
I’m using a metallic mogul type LB as part of a sleeve assembly ( LB + 6” PVC stub through bond plate into basement) for some 4/0 SER cable.

Location requires protection from physical damage due to driveway proximity and I can’t just come into the disconnect with the cable. PVC LB is too small for conductor size.

If the mogul is attached to the service disconnect ( metal enclosure) does it need a bonding bushing ?

2 attachment options.
- Rigid nipple with double locknut and bond bushing.
- PVC MTA and plastic insulating bushing.

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Does need to be bonded, Grounding locknut at panel if there are no concentric/eccentic knockouts, otherwise bond bushing
(You mentioned SER..if you have an outside disconnect..standard locknuts is fine,)
 