Re: Meter and disconnect remote from residence
I was NOT talking about a meter disconnect. I was talking about a packed combination service device with a main breaker immediately downstream of the meter socket.
Here in Ohio, a meter socket MUST have service overcurrent protection as immediately downstream of the socket as practicable. This is the interpretation of every AHJ and power company. This is to keep a short circuit that is beyond the switch from blowing up the meter.
In New Jersey, a central or remote meter without overcurrent protection is absolutely prohibited.
In urban network areas First Energy requires a meter disconnect with current limiting fuses that are of larger rating than the downstream service overcurrent protection. There is no NEC prohibition against this.
Besides, would you want that 150 feet of wiring to have no overcurrent protection? With a redundant service switch at the meter, it is possible to hook up post lights, a shelter for kids waiting for the school bus, or even a power gate.
Also, so called safety sockets that have an unfused disconnect ahead of the meter are in actuality highly unsafe. The reason why is that the power supply in an electronic meter sometimes explodes when energized, particularly on 480 volts. Go over to
www.themeterguy.com .