That wall needs to be demoed because it's collapsing.I don't think there is any rule that says meters have to be located on a wall.
Why can't they leave the part of the wall used by the meters in place? It's not like they would be able to use the space for something else if they leave the meters there.
Are they planning to put a new wall in its place?That wall needs to be demoed because it's collapsing.
yesAre they planning to put a new wall in its place?
I don't think the wall is load bearing. Architect wants to remove the wall and replace the wall with another wall.Is the wall bearing load?
Will the meter bank remain energized?
IMHO the question is 'can the wall be repaired' rather than demolished and replaced.
What is the structure? Concrete blocks, studs and wall board, something else?
Is the surface directly behind the meter bank intact?
Jon
If it is plywood you might be able to separate the plywood from the existing wall and support it temporarily from the front while they demo the existing wall.I don't think the wall is load bearing. Architect wants to remove the wall and replace the wall with another wall.
I think it's brick structure.
behind the meter bank is plywood. Behind plywood is the wall.
How would I support the meter bank from the front without messing with the clearance requirements?If it is plywood you might be able to separate the plywood from the existing wall and support it temporarily from the front while they demo the existing wall.
Can't tell from the photo if this is feasible, but could you put blocking under the meter bank to help support it from the bottom, and attach strut to the plywood on either side of the meter bank, with the strut anchored to the floor and the ceiling, with diagonal braces to the ceiling.How would I support the meter bank from the front without messing with the clearance requirements?
Time to get a new Architect.
Can't tell from the photo if this is feasible, but could you put blocking under the meter bank to help support it from the bottom, and attach strut to the plywood on either side of the meter bank, with the strut anchored to the floor and the ceiling, with diagonal braces to the ceiling.
There's still the issue of reattaching it to the new wall.
How would I support the meter bank from the front without messing with the clearance requirements?
Yes dangerous, but some electricians don't care and are comfortable with working on live equipment lol. How long of a power shutdown are we looking at though? These are tenant meters and we want to minimize disturbance as much as possibleI'd think this would be hella dangerous to do energized.
If the meterbank is shut down for the duration of the wall replacement, do you need to worry about clearance?
De-energized you could build temporary support in front to support everything.
You have electricians doing the demolition work?Yes dangerous, but some electricians don't care and are comfortable with working on live equipment