Meter Base Transfer Switch
aptwes
(Posted this in the 2008 NEC proposals area, but it is really more an issue of code interpretation at this point.)
Our company is a small start-up manufacturing a meter socket/ meter adapter based whole house transfer switch. We are wrapping up design/prototype development and are working with UL to secure a listing. I am not an electrician, nor an electrical engineer, but do have a technical background.
There are clearly some code issues around this product that I need a better handle on before determining what, if any, code proposals might make sense. So I thought I would describe the key points of the device and some of the issues I see, and see what the members of this forum have to say.
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Unit is designed to be used with 120/240v service and a 240v generator input in a non-separately derived system configuration.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">United is intended to be used in "Optional Standby Systems" as described in Article 702.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Basic design is based on interlocking breakers - typically 200 amp service inlet, 30 amp generator inlet.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Generator is cord connected to the switch.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Service input is routed from the lower meter stabs to the service inlet breaker.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Depending on breaker positions, the service or generator input is connected to the lower meter jaws in the existing meter base.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Neutral (grounded conductor) is not switched.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Unit enclosure ground, generator neutral, and generator ground are bonded in the unit.(The generator neutral and generator ground should already be tied together in the generator via a floating connection - I believe). A single connection is then made from this point to the Grounded service conductor in the meter base.</font>
Obviously, we would like to be able to avoid moving the main bonding jumper point.
Does the device fulfill the requirements of a service disconnect?
VI. Service Equipment - Disconnecting Means
230.70 General. Means shall be provided to disconnect all conductors in a building or other structure from the service entrance conductors.
230.75 Disconnection of Grounded Conductor. Where the service disconnecting means does not disconnect the grounded conductor from the premises wiring, other means shall be provided for this purpose in the service equipment. A terminal of bus to which all grounded conductors can be attached by means of pressure connectors shall be permitted for this purpose.
Our device switches the ungrounded service conductors, but does not switch the grounded conductor nor does it provide any other means for disconnecting the grounded conductor. The meter and device would have to be removed to get at the existing connections in the meter base.
IF our device is not a service disconnect then 230.82 might be the place to address it. Perhaps it could be construed as "other current limiting devices" under (1). UL has not yet determined if it will treat it as a meter socket or a meter socket adaptor, so item (2) may not work. Item (3) concerns meter disconnect switches, which are not defined. I suspect our device is not considered a meter disconnect since the connection is severed at the meter outlet rather than inlet, but I do not know for sure. I am also unsure if a case can be made that this would fall under the scope of item (5), but tend to think it does not.
IF the device is deemed to be a service disconnect, then perhaps the language of:
230.72 Grouping of Disconnects. (B) Additional Service Disconnecting Means.
may come into play.
Thanks for your thoughts.
Re: Meter Base Transfer Switch
You are aware that this device already exists and is UL listed? it can be bought outright on the web, or in some cases, a power company offers it for a monthly rental fee, added to their bill.
So you are developing a competitive product?
JP
Yes the is at least one competing product. It is based on different technology and would have some slightly different code issues, I believe. Our device is patented. We believe that for similar applications we will be significantly less expensive and we will offer units with higher generator-side ampacity. All of that business aside, I would like to know what you think about the relevant code issues.
Your equipment is the service disconnect and the main bonding jumper and grounding electrode connection must be made in your equipment. The feed from your equipment to the building panel will require two ungrounded conductors, a grounded conductor and an equipment grounding conductor. To be code compliant the neutral to ground connection(if there is one) in the generator would have to be removed.
Don