Our company is a small start-up manufacturing a meter socket/ meter adapter based whole house transfer switch. WE are wrapping up design/prototype development and are working with UL to secure a listing. I am not an electrician nor an electrical engineer, but do have a technical background.
There are clearly some code issues to be resolved around this product. In trying to draft some code proposals to address this product and related issues, I find I am a bit stumped. So I thought I would describe the key points of the device and some of the issues I see, and see what the members of this forum have to say.
</font>
Obviously, we would like to be able to avoid moving the main bonding jumper point.
Does the device fulfill the requirements of a service disconnect?
VI. Service Equipment - Disconnecting Means
230.70 General. Means shall be provided to disconnect all conductors in a building or other structure from the service entrance conductors.
230.75 Disconnection of Grounded Conductor. Where the service disconnecting means does not disconnect the grounded conductor from the premises wiring, other means shall be provided for this purpose in the service equipment. A terminal of bus to which all grounded conductors can be attached by means of pressure connectors shall be permitted for this purpose.
Our device switches the ungrounded service conductors, but does not switch the grounded conductor nor does it provide any other means for disconnecting the grounded conductor. The meter and device would have to be removed to get at the existing connections in the meter base.
IF our device is not a service disconnect then an amendment to 230.82 might be the place to address it. Perhaps it could be construed as "other current limiting devices" under (1).
UL has not yet determined if it will treat it as a meter socket or a meter socket adaptor, so item (2) may not work. Item (3) concerns meter disconnect switches, which are not defined. I suspect our device is not considered a meter disconnect since the connection is severed at the meter outlet rather than inlet, but I do not know for sure. I am also unsure if a case can be made that this would fall under the scope of item (5), but tend to think it does not.
Also, I am thinking that an amendment to 230.82 may necessitate a related change to:
230.94 Relative Location of Overcurrent Device and Other Service Equipment.
IF the device is deemed to be a service disconnect, then perhaps the language of:
230.72 Grouping of Disconnects. (B) Additional Service Disconnecting Means.
May come into play.
Thanks for your thoughts.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Unit is designed to be used with 120/240v service and a 240v generator input in a non-separately derived system configuration.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">United is intended to be used in "Optional Standby Systems" as described in Article 702.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Basic design is based on interlocking breakers - typically 200 amp service inlet, 30 amp generator inlet.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Generator is cord connected to the switch.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Service input is routed from the lower meter stabs to the service inlet breaker.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Depending on breaker positions, the service or generator input is connected to the lower meter jaws in the existing meter base.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Neutral (grounded conductor) is not switched.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Unit enclosure ground, generator neutral, and generator ground are bonded in the unit.(The generator neutral and generator ground should already be tied together in the generator via a floating connection - I believe). A single connection is then made from this point to the Grounded service conductor in the meter base.</font>
May come into play.