For a supply side connection of a interactive PV system, a service in parallel with the exiting service disconnect is required. The interconnection requires tapping the service entrance between the existing main disconnect and the meter socket. On the case we are addressing the interconnection will be made at a 200A main lugs meter breaker assembly with two branch breakers. One of the breakers is feeding the Main House Panel and the other one is spare. The question is if connecting the Inverter Output circuit to a new backfeed breaker to be installed where the spare one is through the required PV AC disconnect is considered a supply side interconnection or if the two breaker assembly is considered the main AC panel and the interconnection a load side one. If the later, since there is no main, how is the PV system breaker sized?