Meter Can 110.26

Status
Not open for further replies.

VIC1958

Senior Member
2005 NEC..... I cannot find a definite answer if a meter can needs to follow the clearances provide by 110.26. Can some one please help.
 
2005 NEC..... I cannot find a definite answer if a meter can needs to follow the clearances provide by 110.26. Can some one please help.

utility company regulations in our area

"Clearance in front of and to the sides of meter sockets and metering equipment shall be maintained
per NEC Article 110.26 (30-inch width and 36 inches in front of the meter and extend from the
grade, floor, or platform to a height of 6.5 feet or the height of the equipment, whichever is greater). "
 
utility company regulations in our area

"Clearance in front of and to the sides of meter sockets and metering equipment shall be maintained
per NEC Article 110.26 (30-inch width and 36 inches in front of the meter and extend from the
grade, floor, or platform to a height of 6.5 feet or the height of the equipment, whichever is greater). "

Would the measurement be made from the front of the enclosure or the front face of the meter?
I have seen the clearances violated consistently around here.
 