Hi, the utility company I work for, requires a residential customer to install a ground rod at the meter to ground the neutral at that point. The question recently came up of whether or not the customer can use that rod as a GE as long as they do not run the GEC from the main panel through the meter can to the ground rod per company policy.
I don't have a problem personally with the customer running a GEC sized per 250.66 from the main panel to the ground rod and using it as a GEC, as long as they do not run the GEC through the meter can, however, that ground rod at the meter is typically there for communications companies to bond to, as I understand it.
It also brings up the issue of, does this meet 250.52 through 250.56. I think it might depending on what other approved electrodes were used and if they were considered to be present.
I know that I do not enforce NEC on anyone, just looking for some opinions on this situation.
What do you guys out there do in residential installations for your GES?
I don't have a problem personally with the customer running a GEC sized per 250.66 from the main panel to the ground rod and using it as a GEC, as long as they do not run the GEC through the meter can, however, that ground rod at the meter is typically there for communications companies to bond to, as I understand it.
It also brings up the issue of, does this meet 250.52 through 250.56. I think it might depending on what other approved electrodes were used and if they were considered to be present.
I know that I do not enforce NEC on anyone, just looking for some opinions on this situation.
What do you guys out there do in residential installations for your GES?