Meter Can Height

Status
Not open for further replies.
Is there a code rule to how high a meter can be mounted. I have looked hi & lo through the 2002 & 2005 NEC and have not been able to find an answer besides readily accessable or is it up to the AHJ.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Meter Can Height

That is up to the power company. Ask them. In most cases they want 5 to 5'6" to the center of the meter.
Don
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Re: Meter Can Height

Just a follow up to Don's post, it's not an NEC issue but a POCO issue. Most of the POCO's in my area require the height to be 4'6" to 5'6" to the center of the meter. However, there are some exceptions : 1) Where a walkway or driveway is within 2' of the face of the meter some will require the meter height to be 6'6" to the top of the meter pan in order to avoid accidental damage; 2) Where it is impractical to mount the meter pan under normal conditions due to the structure of the building some POCO's require a minimum height of 3'0" to the top of the meter pan.
 

charlie

Senior Member
Location
Indianapolis
Re: Meter Can Height

Also, every electric utility has different rules. We want 6 ft to the top of the meter cabinet or 5 ft to 6 ft to the top of a meter fitting. We also have exceptions to those rules and also requirements for the location. :D
 