Hello,
I will be conducting a project soon and I wanted to inquire about what are the rules now since we got the new NEC 2020 Book to abide by.
According to 230.85
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped.
Does anyone know how this would affect my work?
Would I need to install a disconnect for the apartment complex?
If so, would I need a disconnect per meter can? or per meter entity?
Please advise,
Thank you!
I will be conducting a project soon and I wanted to inquire about what are the rules now since we got the new NEC 2020 Book to abide by.
According to 230.85
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped.