Meter Can Replacement in Apartment Complex

Status
Not open for further replies.

Louix5

New User
Location
Norcross, GA 30093
Occupation
Service Coordinator
Hello,

I will be conducting a project soon and I wanted to inquire about what are the rules now since we got the new NEC 2020 Book to abide by.

According to 230.85

230.85 Emergency Disconnects.

For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped.

Does anyone know how this would affect my work?

Would I need to install a disconnect for the apartment complex?

If so, would I need a disconnect per meter can? or per meter entity?

Please advise,

Thank you!
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Hello,

I will be conducting a project soon and I wanted to inquire about what are the rules now since we got the new NEC 2020 Book to abide by.

According to 230.85

230.85 Emergency Disconnects.

For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault
The eording of this section is poor, and had resulted in many questions here.

Does anyone know how this would affect my work?
>>Need emergency disconnect if its a 1 or 2 family dwelling

Would I need to install a disconnect for the apartment complex?
>> NEC does not use term apartment.

If so, would I need a disconnect per meter can? or per meter entity?
>>>Disconnects are for service conductors.

Please advise,

Thank you!
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
How many units in the building? If there are more than two, the new rule in 230.85 does not apply. It only applied to one and two-family dwelling units.
 

david

Senior Member
Location
Pennsylvania
Hello,

I will be conducting a project soon and I wanted to inquire about what are the rules now since we got the new NEC 2020 Book to abide by.

According to 230.85

230.85 Emergency Disconnects.

For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped.

Does anyone know how this would affect my work?

Would I need to install a disconnect for the apartment complex?

If so, would I need a disconnect per meter can? or per meter entity?

Please advise,

Thank you!
From what you posted only one disconnect is required
 