I was given a set of plans for a solar install ,grid tied with battery back up. Background. Existing underground service enters a meter at a residence from underground and then nipples directly into the 200 amp MDP. The MDP is where all the bonding takes place
9 I would prefer to leave it that way)
Design...
A meter collar is designed to be used as the "transfer switch". (not really a transfer switch rather a utility disconnect)
However the utility has not yet approved the meter collar for their meter. ( not uncommon) So we are going to add a meter can and collar down stream.
The plans show the following. Utility Meter> 200 amp disconnect>meter can w/meter collar>MDP. Can I eliminate the 200 disconnect in the plans set therefore eliminating having to rewire the MDP as a sub panel.
I would like to go. Utility meter> customer meter/metercollar>MDP. Not having to change the point of bonding would be nice.
I have never seen this but it may be possible The meter cans are both service rated. Is there any reason two meters can't be installed before entering the MDP?
Thanks in advance
G-
9 I would prefer to leave it that way)
Design...
A meter collar is designed to be used as the "transfer switch". (not really a transfer switch rather a utility disconnect)
However the utility has not yet approved the meter collar for their meter. ( not uncommon) So we are going to add a meter can and collar down stream.
The plans show the following. Utility Meter> 200 amp disconnect>meter can w/meter collar>MDP. Can I eliminate the 200 disconnect in the plans set therefore eliminating having to rewire the MDP as a sub panel.
I would like to go. Utility meter> customer meter/metercollar>MDP. Not having to change the point of bonding would be nice.
I have never seen this but it may be possible The meter cans are both service rated. Is there any reason two meters can't be installed before entering the MDP?
Thanks in advance
G-