eric stromberg said:
Bob,
You mentioned that the meter disconnect is unfused.
Why is this? ?
Eric first off I should make clear I have never seen a meter disconect.
I have read that meter disconnects are used to solve a possible code conflict.
If the power company requires cold sequence metering the service disconect with its fuses and GEC connection may become inaccessible as the power company may seal off access to the unmetered conductors.
Having the Overcurrent devices inaccessible is a violation of 240.24(A)
Having the GEC connection inaccessible is a violation of 250.24(A)(1)
We have bend around this sometimes. The POCO will seal the covers to the service disconnect when it is ahead of a switchboard full of tenant meters. The manufacturer puts the MBJ connection in the same section as the service disconnect. We normally say a sealed POCO section is inaccessible, but it really isn't. I mean a couple little seals???
By allowing a non fused meter disconect switch ahead of the meter and a service disconect after the meter both the NEC and the power company needs can be met.
eric stromberg said:
Second question. Are these disconnects rated for breaking the circuit while under load
I do not know.