erickench
- Brooklyn, NY
I see here a possible misinterpretation of the NEC on the part of manufacturers in regards to connecting the grounded conductor to meter enclosures. NEC 250.24(C) contains specific wording in that it state's:
Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be run to each service disconnecting means and shall be connected to each disconnect means grounded conductor(s) terminal or bus. A main bonding jumper shall connect the grounded conductor(s) to each service disconnecting means enclosure.
However, I do not see any similar wording for meter enclosures. NEC 250.92(B) give's rules for bonding service enclosures together which would seem to make it a violation to use PVC nipples or even to bond just one end of the connecting metal raceway between the service enclosures. NEC 250.174 would give rules for earth grounding meter cases in systems that are 300 volts or more to ground which can be accomplished via connection to the equipment grounding conductor.
I know we had a similar discussion on another thread on this topic but I would like to hear more.:slaphead: