m73214 said:I believe the OP's question was does he need a disconnect below the meter on the pole. I raised this question a while back and was told that yes, in a situation like this, the to be pole is considered a "structure" and therefore needs a disconnect.
m73214 said:So Cavie....are you saying that in a situation where we have a remote service point on a pole with a meter, we don't need a disconnect until the service entrance conductors enter the building served?
In our area many POCOs require a remote meter, but no disconnect. Yes its a structure, I agree.m73214 said:I believe the OP's question was does he need a disconnect below the meter on the pole. I raised this question a while back and was told that yes, in a situation like this, the pole is considered to be a "structure" and therefore needs a disconnect. I thought a disconnect on the dwelling would suffice. For example, if I have a meter mounted to a dwelling and run the service entrace conductors 100' on the outside of the dwelling and then go into an interior panel, as long as the panel has a main breaker, I'm compliant. So, back to the OP's question, he would need a disconnect on the pole and another at the dwelling, correct?
schultze said:I have a customer owned 6x6 post 50' from a house. Power is fed from overhead and then goes under ground to house. Can I put the meter on the post without a disconect and then feed a 200 amp main at house.