When installing a new overhead combination service for a residential service replacement we were told by the EI that we could not install our romex cables coming from under the house in a single 2" pipe approx. 30" in length with an LB and a nipple at the lower end into the bottom of the panel. We have always done this and have NEVER been called on it in the past.
The inspector cited Article 312.5 C which states that cables "shall be permitted" to enter from the top of the "cabinet, cut-out box or meter socket enclosure" in the above manner if all of conditions (a-g) are met. In order to enter from the bottom, we would have to first terminate all of the cables in a junction box under the house and then run via the conduit connected to the junction box up to the bottom of the loadcenter/meter comb.
My question is this: Is he right that this precludes having any cables at all from entering from the bottom without first terminating at a j-box? If so why? What is the intent here, that you can enter from the top and not the bottom?
Any help on this would be appreciated.
Don
Valley Isle Electric, Maui
The inspector cited Article 312.5 C which states that cables "shall be permitted" to enter from the top of the "cabinet, cut-out box or meter socket enclosure" in the above manner if all of conditions (a-g) are met. In order to enter from the bottom, we would have to first terminate all of the cables in a junction box under the house and then run via the conduit connected to the junction box up to the bottom of the loadcenter/meter comb.
My question is this: Is he right that this precludes having any cables at all from entering from the bottom without first terminating at a j-box? If so why? What is the intent here, that you can enter from the top and not the bottom?
Any help on this would be appreciated.
Don
Valley Isle Electric, Maui