Therealcrt
- Kansas City
- Electrician
A family friend of mine who lives in a townhouse called me over because they are 150 amp meter main breaker has tripped for the second time in three days. The first time was Saturday. The second time was tonight. He reset it both times but tonight when he tried to reset it, it would not go on, so he called me over I looked inside the panel in the garage, which is a main lug 100 amp panel. All breakers were on. I turned on all appliances, ran everything I could, and did an amp clamp on both legs it’s single phase by the way with all appliances running, and lights on each phase was drawing around 40 to 50 A when I went outside to the meter bank I took the cover off and tested those wires as well. I got the same result the voltage was correct as well. 120 240 after 10 minutes the meter main tripped so I checked for loose connection at the main breaker. Everything was tight but one leg was really really hot to touch The other was not. my conclusion is a bad 150 amp main breaker. I did all the troubleshooting I thought was necessary is my conclusion, correct or what else could it be?