New construction with a meter pan, generator automatic transfer switch (ATS) and main breaker panel all on an outside wall with PVC nipples connecting all three metal enclosures. Utility service is underground. The neutral bus in the meter pan is bolted/bonded directly to the meter pan enclosure.
I have it currently wired a shown in Meter Pan 1 drawing. With it wired this way I have a parallel neutral connection between the meter pan and the ATS. So I think I should remove the bonding jumper between the meter pan and the ATS as shown in Meter Pan 2 drawing. The POCO's Service Specification Book appears to show that it should be wired as shown in Meter Pan 3 drawing.
I looked at 250.24 and it says the MBJ needs to be in the enclosure with the service disconnect but I don't see where it says the GEC needs to be in that same enclosure, just that it needs to be connected to the grounded service conductor somewhere between where the underground service comes into the meter pan and the first disconnect. They say it needs to be "accessible" which sounds like the meter pan would be "accessible" even with the POCO wire lock on it since it doesn't say "readily accessible". Thoughts?
I have it currently wired a shown in Meter Pan 1 drawing. With it wired this way I have a parallel neutral connection between the meter pan and the ATS. So I think I should remove the bonding jumper between the meter pan and the ATS as shown in Meter Pan 2 drawing. The POCO's Service Specification Book appears to show that it should be wired as shown in Meter Pan 3 drawing.
I looked at 250.24 and it says the MBJ needs to be in the enclosure with the service disconnect but I don't see where it says the GEC needs to be in that same enclosure, just that it needs to be connected to the grounded service conductor somewhere between where the underground service comes into the meter pan and the first disconnect. They say it needs to be "accessible" which sounds like the meter pan would be "accessible" even with the POCO wire lock on it since it doesn't say "readily accessible". Thoughts?