DBrenchley
Member
- Location
- Cayo District Belize CA
- Occupation
- Retired EE
Is it permissable to use the upstream line lugs of a multi meter panelboard for line distro to additional meter boxes?
TY. Let me explain the sit I find myself in for those scratching their heads over my recent posts. 1. I am not a licensed electrician but have extensive experience in entertainment under article 520 NEC. You know the one that allows you to break all the rules set forth elsewhere in the text. Therefore I am not well versed as I should be. Hence my basic questions.The lugs will have to be rated for the number of conductors terminated
Keep in mind the "six disconnect rule"
A load calculation might well be required.
Care will need to be taken on terminating the 200 amp cable on the 100 amp equipment.
There is no multi-service meter main combos on the market that meet the requirements of the rules in the 2020 NEC, and there won't be for some time as UL 67 has been modified to define compartment as used in that code rule. The definition is that the compartment must comply with the rules in UL 50 for junction boxes.K. Watched your video on six disconnect rule. I'm as confused as much as you folk's seemed to be. In this install a 4 meter panelboard has a two pole fuse disconnect at the service feed. Each meter occupies what I would consider a compartment. eg the meter and associated disconnect can be serviced w/o exposure to the panels main buss. In your opinion do we meet the spirit of the rule or might we be required to replace the panelboard if we chose to upgrade the service?
Dang. Kinda put the industry between a rock and a hard place. Any one have real life experience eg upgrading service to a meter bank? Are inspectors forcing replacement of the panels?There is no multi-service meter main combos on the market that meet the requirements of the rules in the 2020 NEC, and there won't be for some time as UL 67 has been modified to define compartment as used in that code rule. The definition is that the compartment must comply with the rules in UL 50 for junction boxes.
Why did I assume the code change was inspired by or done in cooperation with product standard revisions? Sheesh.There is no multi-service meter main combos on the market that meet the requirements of the rules in the 2020 NEC, and there won't be for some time as UL 67 has been modified to define compartment as used in that code rule. The definition is that the compartment must comply with the rules in UL 50 for junction boxes.
UL was dragging their feet on this safety issue so the NEC drove the change. Sometimes it works the other way.Why did I assume the code change was inspired by or done in cooperation with product standard revisions? Sheesh.
IMO the NEC needs to stay in their damn lane. They are not gods, they can't have their way with everything. I actually am on the verge of thinking the feds need to step in and regulate the out of control NFPA.UL was dragging their feet on this safety issue so the NEC drove the change. Sometimes it works the other way.
Actually those changes were a result of PIs of mine that triggered other PIs. I had given up after trying for three code cycles, but a couple of cyces later others proposed changes to both the NEC and UL 67.IMO the NEC needs to stay in their damn lane. They are not gods, they can't have their way with everything. I actually am on the verge of thinking the feds need to step in and regulate the out of control NFPA.
I actually fully agree with you that most panelboard designs are ridiculous and should be designed with better barriers, covers and compartments. The I-line design is good. But that said, I also stand by my opinion that this is not an NEC issue and they should have kept their fingers out of it.Actually those changes were a result of PIs of mine that triggered other PIs. I had given up after trying for three code cycles, but a couple of cyces later others proposed changes to both the NEC and UL 67.
We need to have 100% isolation of the service line side connections and OCPD like they have in Canada. My original PIs were based on the Canadian design for service equipment as the same manufacturers that make service equipment for the US, also make service equipment for Canada.
The NFPA has no control over anything..they are a private organization that writes codes and standards...there is no control until some unit of government adopts those codes or standards.
I actually fully agree with you that most panelboard designs are ridiculous and should be designed with better barriers, covers and compartments. The I-line design is good. But that said, I also stand by my opinion that this is not an NEC issue and they should have kept their fingers out of it.Actually those changes were a result of PIs of mine that triggered other PIs. I had given up after trying for three code cycles, but a couple of cyces later others proposed changes to both the NEC and UL 67.
We need to have 100% isolation of the service line side connections and OCPD like they have in Canada. My original PIs were based on the Canadian design for service equipment as the same manufacturers that make service equipment for the US, also make service equipment for Canada.
The NFPA has no control over anything..they are a private organization that writes codes and standards...there is no control until some unit of government adopts those codes or standards.
If they don't adopt and something happens fingers get pointed at them. Most government types aren't smart enough to understand the circuit in a dollar store flashlight, so they just follow the herd.but most just blindly adopt.
I have not read it but I know of it.If they don't adopt and something happens fingers get pointed at them. Most government types aren't smart enough to understand the circuit in a dollar store flashlight, so they just follow the herd.
Have you ever read "Atlas Shrugged?
First, was there a more pressing reason (injuries, deaths, fires that were occuring) than just imitating the Canadians?...
We need to have 100% isolation of the service line side connections and OCPD like they have in Canada. My original PIs were based on the Canadian design for service equipment as the same manufacturers that make service equipment for the US, also make service equipment for Canada.
...
Our product standards and the ones used in Canada are not the same for this. A product listed to a Canadian standard and not to a US standard cannot be used in the US. US manufacturers won't produce a product until there is a product standard.First, was there a more pressing reason (injuries, deaths, fires that were occuring) than just imitating the Canadians?
Second, if the same manufacturers make this stuff for the Canadians for years, why are we saying that this code change has led to unavailability of meter banks because manufacturers don't have designs?