I agree 44 amps..... however note this is NOT the peak amps. This is demand which is (usually) the highest 15 minute average.Hi all,
Just wanted to make sure I'm reading the electric bill correctly. If I want to figure out the highest amp draw for a particular month, I use 'demand actual' correct? In this case, it would be 15.84 KW... and at 208 volts, 3 phase, I'm calculating 44 amps. Is this correct?
View attachment 2562318
Is there a way to calculate the peak amps?I agree 44 amps..... however note this is NOT the peak amps. This is demand which is (usually) the highest 15 minute average.
Generally not from typical utility bill.Is there a way to calculate the peak amps?
Note also you need an extra 25% if using 220.87. so with that and some addition for power factor, I wouldn't worry about finding the true instantaneous peak .Thanks.
Actually, with the 44 amps calculated above, I should also divide by a 0.8-ish power factor and bump it up to 55 amps... just to take into account KVA.
Got it... thanks!Note also you need an extra 25% if using 220.87. so with that and some addition for power factor, I wouldn't worry about finding the true instantaneous peak .