Yes, but the definition of a compartment in UL 67 for this application is an enclosure that meets the requirements of UL 50, the product standard for junction boxes. Don't think that there are any on the market with more than two compartments.Can't the multiple service disconnects be in separate compartments of the same enclosure?
Siemens has 2 through 6 meter/disconnect models.Yes, but the definition of a compartment in UL 67 for this application is an enclosure that meets the requirements of UL 50, the product standard for junction boxes. Don't think that there are any on the market with more than two compartments.
The rule has nothing to do with shutting down multiple service disconnects. All of my proposals were asking for each service disconnect to be in a separate compartment from any load side conductors or breakers, like is required in Canada,I can see the safety factor in larger commercial/industrial equipment but for residential equipment its not hard to shut off 2 or 3 service disconnects.
If the line side of the disconnects are insulated what is the issue with having multiple disconnects in single enclosure?The rule has nothing to do with shutting down multiple service disconnects. All of my proposals were asking for each service disconnect to be in a separate compartment from any load side conductors or breakers, like is required in Canada,
little pieces of insulating material do little to reduce the potential of an arc flash, they are only intended to provide shock protection.If the line side of the disconnects are insulated what is the issue with having multiple disconnects in single enclosure?
Having a single or multiple disconnects doesn't change how the circuit breakers are insulated. A single circuit breaker will often have the same piece of flexible plastic covering the line connections. I would be in favor of having a separate secure metal barrier covering the line conductors/bussing and breaker lugs.little pieces of insulating material do little to reduce the potential of an arc flash, they are only intended to provide shock protection.
240 single from a relatively high impedance transformer secondary and conductors. Do you personally (not code) think there is much potential for an arc flash event?little pieces of insulating material do little to reduce the potential of an arc flash, they are only intended to provide shock protection.
That was in one of my rejected proposals.Having a single or multiple disconnects doesn't change how the circuit breakers are insulated. A single circuit breaker will often have the same piece of flexible plastic covering the line connections. I would be in favor of having a separate secure metal barrier covering the line conductors/bussing and breaker lugs.