Milbank makes a tap lug that will replace the existing slide in lugs that will accommodate the existing wire under the lug in the meter and an additional lug for up to a 100 amp tap from a meterbase on the load side.
My question is if you have a 200 amp meterbase with 200 amp wiring up the mast, doesn't the tap lug create the possibility of overloading the wiring up the mast since it is ahead of the first 200 amp limiting overcurrent device?
Say you had a 200 amp meterbase on a pole out in the yard with 200 amp wiring up the mast with a 200 amp overcurrent device below it that fed a panel in the house 100' away.
Then the owner builds a garage 100' away from the meter but its closer to the meter location on the pole than the house.
would installing these tap lugs on the load side of the meter then installing an additional 100 amp OCPD at the pole to feed the new garage be a code violation since the wiring up the mast could become overloaded? not likely but possibly.
I could see them working if the 200 amp OCPD that protected the feeder to the house was reduced to a 100 amp OCPD and the feeder to the garage had a 100a OCPD below the meter at the pole, but that would defeat the purpose.
JAP>
My question is if you have a 200 amp meterbase with 200 amp wiring up the mast, doesn't the tap lug create the possibility of overloading the wiring up the mast since it is ahead of the first 200 amp limiting overcurrent device?
Say you had a 200 amp meterbase on a pole out in the yard with 200 amp wiring up the mast with a 200 amp overcurrent device below it that fed a panel in the house 100' away.
Then the owner builds a garage 100' away from the meter but its closer to the meter location on the pole than the house.
would installing these tap lugs on the load side of the meter then installing an additional 100 amp OCPD at the pole to feed the new garage be a code violation since the wiring up the mast could become overloaded? not likely but possibly.
I could see them working if the 200 amp OCPD that protected the feeder to the house was reduced to a 100 amp OCPD and the feeder to the garage had a 100a OCPD below the meter at the pole, but that would defeat the purpose.
JAP>